Jump to content

PIT

Members
  • Posts

    2
  • Joined

  • Last visited

PIT's Achievements

Newbie

Newbie (1/4)

0

Reputation

  1. Thanks I'll give it a try and let you know how it goes.
  2. I am having a little trouble making the display reading on the V290-E1B read what my Sc1000 controller from Hach is reading on the NTU. For example the Sc1000 would read 0.265NTU and then the PLC would read just 0.2 but I want it to read accordingly.I tried moving the decimal on the settings but all it does is move the 2 before or after the decimal. I am using a 4-20mA signal and a linear function in my ladder and just that. Does anyone have any suggestions?
×
×
  • Create New...