  1. Hi all, We are currently trying to figure out (we are newbies at visilogic) how to use a vision controller to have a user hit a button and for it to print the PLC screen to a printer. Is this even possible? If not, is it possible to print a set of data collected through the PLC (like pressure sensor data) WITH a graphical logo of our company? Thanks for any answers!
  2. Thanks for the input Damian! I am using 4-20ma and the jumpers are set correctly for such according to the manual. I've attached a quick drawing on the wiring, so maybe that can help you figure out what might be wrong. Remember it is showing a value for the output, it is just not changing.
  3. Hi there, I recently started learning how to run visilogic on one of our v570 PLCs at work, but I've run into a problem when trying to input the analog signal of our SMC ITV3000 electronic regulator. I am able to fully control the output from the PLC and control the pressure output, however I am unable to retrieve a changing analog monitor signal. I believe I have all connections correct, and the logic in my problem should be solid. (however, even the hardware input MI doesn't read correctly) Basically what is happening is I am getting a positive point value (around 250) however it does not change at all. So this is telling me that the signal is still being inputted, but that it is not proportional to the actual pressure, obviously. Please let me know if you need any more information about my project and I will gladly add it to this thread. Any help would be appreciated! Thanks!
×
×