Hi Guys, I was thinking that it will be very useful to have min and max value limit entries option for the timer Preset entry for Vision series. In the following star-delta motor starting example, i use T1 as a delay in order to make sure that star contactor will be de-energised before delta contactor is energized. Even though i use electrical interlock circuitry to prevent short-circuit, i always prefer to provide also an electronic safety. Since response time of the PLC outputs is much faster than the response time of the contactor coils, T1 delay is required. Today i had a call from one of my customers saying that there is something wrong with the motor of his air pressure booster which is controlled by a V130. The problem was that someone changed T1 preset value from 00:10 to 10:00 by mistake (10sec instead of 100mS). Just a practical example of a problem in the real world!