Hi everyone!
I'm having some doubts. I configured the PID Config FB and after that I did an AutoTune.
I tried to run the PID control loop energizing the "PID A.Tune RUN" FB and it worked very good, but I have some questions.
Once I finish my PID Control loop, do I need to reset numeric MI associated to Control Output value? If I don't do that, it remains with the last value before de-energize the "PID A.Tune RUN" FB so the Duty Cycle of PWM associated to that Control Output does not go to zero.
Another question: when I de-energize the "PID A.Tune RUN" FB, the PID Status message is still 4, so it's like the PID is Running, but that's not true because it stop. Is that a kind of VisiLogic bug or am I doing something wrong?
Thanks in advance,
Gonzalo.