Chris2 Posted January 30 Report Share Posted January 30 Hi, Is it possible to use a single Unistream Lite HMI to connect to 2 x Unistream PLC's via the VNC facility? Or can you only have the one VNC connection. The HMI Lite would be need to display the screens from the two unistream PLC's. Link to comment Share on other sites More sharing options...
Easy Pete Posted January 30 Report Share Posted January 30 At the same time? No. But you can connect lets say 2 PLCs and modular panel acting as Unistream display to the same switch, (TL-SG605 for example). Then you set network settings for all devices, example bellow and you can access both PLC's from that panel. You can also save addresses, so you only switch from Connection 1 and Connection 2, no need to input everything again. Also connect PC with right network settings and you see all 3 devices. Be careful with giving switch internet access, if you do set passwords on all devices. PLC 1: IP 192.168.1.85 PLC 2: IP 192.168.1.86 Panel: IP 192.168.1.87 Mask 255.255.255.0 Gateway 192.168.1.254 BR E.P. Link to comment Share on other sites More sharing options...
Chris2 Posted February 21 Author Report Share Posted February 21 Hi Easy Pete, Sorry, I didn't realise I had a reply. Thank you for detailed response. I will make a note of this method. Thank you again. Chris Link to comment Share on other sites More sharing options...