Dear,

I'm trying to configure and use modbus rtu communication on my V1210, but I'm experiencing failures. When accessing the PLC's service mode, I noticed that the COM2 port keeps alternating between Modbus and PCOM randomly.
I programmed the communication on the ladder as per the help instructions, the COM dipos were changed to RS 485, that is, in the physical and programming part everything seemed to be ok.

 

I added this program I made just to test communication with ModbusPool

TesteDAKOL.vlp

Link to comment
Share on other sites

  • MVP 2023

Please use MODBUS Example project code (from Visilogic Help menu) for setup master or slave.

The read instruction is called in every run of the program - it doesn't work like that.

Modbus is a slow network and when you force every program scan to try to transmit a request - the PLC can't do it.

Study the example code and use it  for your case. Also check that the dip switches on the back of the PLC for port2 are configured correctly and that the correct cable is used.

Link to comment
Share on other sites

  • MVP 2023

Modbus is a network where the master and slave interact only if all the requirements for establishing a connection are met.

These are the following requirements:

- the wires that physically connect the master and slave are connected correctly (they are often connected incorrectly).

- the PLC port is configured correctly using dip switches. 1 and 6pin of PLC port2 used for RS485 and it function selected by DIP SW on PLC back.

- Speed and port settings are the same for maser and slave.

- The master sends the correct function codes supported by the slave. The table of available function codes for the V1210 PLC as slave is in the help in the Modbus section.

- numbering of cells (that is, addresses) may physically differ by one (+1). That is, the cell in the PLC with the address 0 can be cell 1 in the program you use, that is, there is some shift (related to the different interpretation of the concept of "first" cell - is it counted from 0 or from 1). But it depends on the device you connect and the program you use.

 

Link to comment
Share on other sites

  • MVP 2023

There are numerous references all over the forum to modbus issues. 

The very first thing that should be done with any new device is to find out how it communicates correctly by using your PC running any of the numerous free programs available.  Once you know all the aspects you then move this to the PLC.  It makes it vastly easier.

In your case you then need to learn the various aspects of how the PLC does what you have previously learnt via the PC.  Always bear in mind Kratmel's most important bit of advice above..... 

4 hours ago, kratmel said:

Modbus is a slow network and when you force every program scan to try to transmit a request - the PLC can't do it.

You need to arrange your ladder accordingly.  Having your retries at 3 is compounding the problem of expecting racing car speeds when you're working with a tortoise.  Use your PC testing to see what is the highest speed you can actually  achieve....start at 9600 or less and slowly increase until you get error.  And then understand that this speed may not be possible on the actual installation.

For what it's worth, I don't have anything as ID 1.

 

 

Link to comment
Share on other sites

Dear,
Very grateful for everyone's support
I'm just configuring and testing the Modbus network communication, I haven't 
programmed the writing and reading conditions yet. What is happening is a difficulty 
in carrying out communication in RTU, in the images I am sending I did the same procedure 
but using Modbus IP, notice that it worked in IP, the failure in RTU is very strange, I configured 
the dips in rear of the PLC, I configured the COM INT everything apparently correctly, what is 
strange is seeing in the Info Mode of the PLC the COM 2 port switching from Modbus to PCOM alone

 

 

Visilogic.jpeg

ModScan32.jpeg

Link to comment
Share on other sites

Dear

I was able to establish ModBus RTU communication, the pinout 
of the RJ11 cable was inverted in relation to my USB/RS485 converter, 
the names A and B were connected the same in the PLC and in the converter,
 I changed wires A and B in the converter and it communicated. 
Thank you very much for everyone's support
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.