David Thomas Posted November 12 Report Posted November 12 I have two Festo servo drives and I am trying to communicate via Modbus TCP with the Vision 1210 set as a Master. After a lot of research and trial an error, I have been successful writing a project to control one of the Festo servos. I am trying to communicate with the second Festo Servo and I am having issues closing the port and establishing a connection to the second servo using TCP IP Connect and TCP IP Close. When I try to close the port, I cannot write to the first device and the read data comes in slowly. I am sure it is do to the sequencing of opening and closing the ports. I have looked at all the examples but not sure what to do at this point. Does anyone have an example or some suggestions at how I can sequence the opening and closing of ports? Thanks in advance, mdavidthomas Visilogic V9.9.0 Vision1210 _ModbusTCP_CMMTASMP_V5c.vlp
MVP 2023 Flex727 Posted November 18 MVP 2023 Report Posted November 18 You have 4 sockets available for Ethernet communications. Use a separate socket for each servo drive and you will not need to open and close your MODBUS connections.