richie Posted December 19, 2011 Report Share Posted December 19, 2011 I loaded my project on 1040 hmi with v200-18-e3xb module, all my inputs work but none of my outputs work. i tried just a simple program and still nothing. I can monitor the program and it shows that the output is on but the relay never close. this is all new hardware any one got a clue. i think it is just a bad v200 plug in module. Quote Link to comment Share on other sites More sharing options...
MVP 2021 Joe Tauser Posted December 19, 2011 MVP 2021 Report Share Posted December 19, 2011 Did you wire power to the V1 and V2 terminals? See page 4 and 5 of the spec sheet- the relays won't work if you don't. Joe T. Quote Link to comment Share on other sites More sharing options...
AlexUT Posted December 19, 2011 Report Share Posted December 19, 2011 Hi richie, V200-18-EX3B is isolated from OPLC. You need connect power to "24VDC DIGITAL OUTPUTS". Contacts are located right-side under "ANALOG OUTPUTS". Relay starts to work (click). Quote Link to comment Share on other sites More sharing options...
richie Posted December 19, 2011 Author Report Share Posted December 19, 2011 Did you wire power to the V1 and V2 terminals? See page 4 and 5 of the spec sheet- the relays won't work if you don't. Joe T. thanks joe that was the problem. Quote Link to comment Share on other sites More sharing options...