RS232 cable


Recommended Posts

I have a M91 into a box. I would like to have a acces to the RS232 port for troubleshooting whithout open the box. I connect the cable to a coupler like that: (http://www.digikey.ca/product-search/en?x=0&y=0〈=en&site=ca&KeyWords=a34359-nd) but the plc don't want communicate. I check the continuity for both cables and is ok. I there a maximum length for rs232? When I plug the plc direct to the pc with one cable is ok. When I connect two cable with the coupler don't work.

Thanks

 

Link to comment
Share on other sites

  • MVP 2023

The typical RJ-11 cable (like used for phones and like what comes with the PLC) is a crossover cable. If you add an additional cable between the PLC and the coupler it must be a straight-thru cable like this one:

http://www.monoprice.com/Product?c_id=102&cp_id=10222&cs_id=1022201&p_id=928&seq=1&format=2

 

You are probably doing a double crossover which will not work. Two crossover cables WILL only work if the coupler is also a crossover.

 

Where I work we do exactly what you are trying to do and encountered the same issue you are having. A straight-thru cable inside the box works perfectly.

  • Upvote 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...