Can i use the read immediate input as high speed counter. Is it necessary to use read immendiate input in _Interrupt 1.25 mS or i can use it in a normal subroutine.

Hi Sunit,

The principle behind the  Immediate functions is to access I/O information (read/write) regardless of the PLC scan time (as you probably know - the PLC scan is a loop, starting with reading the inputs, then performing the ladder logic and finally activating the outputs).

Regarding using this feature as a high speed counter - the answer is no. that is because the normal digital input has a delay response much slower than the typical scan time (usually 10ms).

Link to comment
Share on other sites

  • MVP 2023

Kind of.  As Eyal points out, regular inputs are slower than HSC inputs.

 

You will have your best luck using inputs on the PLC's main I/O board.  It doesn't work with expansion modules.  Set up the 1.25 ms Interrupt subroutine and put your Immediate Input blocks in it, along with any logic such as incrementing an MI.  Be sure to use a positive transition on the input you've just read.  Also don't forget that the input has to be off for at least one execution of the Interrupt routine, so your actual response time is 2.5 ms, which translates to 400 Hz.

 

If you can live with a 400 Hz response time it will work.

 

Joe T.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...