ZoranM Posted January 18, 2016 Report Share Posted January 18, 2016 Hi, I`ve installed V130 with simple web server application, at remote facility. I ve succeed to connect remote web server from control centers PC and it looks like it is working fine but ocationally link breaks. Rebooting either remote router (HG531 v1 Firmware version HG531V1V100R001C90B017) or V130 recoveres the link. I ve set SB 168 already but problem persists. Is there any other way to automate lost link recovery process? Quote Link to comment Share on other sites More sharing options...
Ofir Posted January 18, 2016 Report Share Posted January 18, 2016 Hi, It seems that somehow the socket was were not closed properly and this might be the reason there is no option to reconnect . Please set a power up value of 50 to SI103 – SI106 Keep alive according to the socket number you are using. (This is in units of 100ms) For example if you are using socket 0 then set a power up value of 50 to SI103. This enables the PLC to close the socket if there is no communication from the connected device. 1 Quote Link to comment Share on other sites More sharing options...
ZoranM Posted January 20, 2016 Author Report Share Posted January 20, 2016 Hi, It seems that somehow the socket was were not closed properly and this might be the reason there is no option to reconnect . Please set a power up value of 50 to SI103 – SI106 Keep alive according to the socket number you are using. (This is in units of 100ms) For example if you are using socket 0 then set a power up value of 50 to SI103. This enables the PLC to close the socket if there is no communication from the connected device. I ve applied advised settings. During last 24h there haven t been any permanent link breaks. It seems the problem is solved. Thanks! Quote Link to comment Share on other sites More sharing options...