gsimpson Posted January 23, 2016 Report Share Posted January 23, 2016 Hello, I have a problem communicating to an Omron MX2 VFD using RS485 MOBUS with a V430. Basically I have all of the required FB's for MODBUS Serial. The port is configured, the MODBUS protocol is confured, the drive is configured. I can monitor the queries and responses on the HMI in Config mode and see that the data is exactly as is should be. I can also see the data change in the drive parameters. The problem I have is that in Visilogic, I never see the data from the queries. For instance, I will execute a Read Coil (Function #1). I have all the correct parameters set. The actual data monitored on the HMI shows the data as I expect it to be (at least 1 coil is high). But in my logic, I never see the data on the output side of the FB. I also see the total sessions increment by one every time it is executed, but the Acknowledgment number never changes (it's always been 0). I also never see anything other than 0 for the status (which indicates no problems). I don't understand what I might be missing and any insight would be helpful. Hardware: V430-J-R34 Omron 3G3MX2 Inverter Config: V430: Node 1, Comm 1, RS485, 57600, 8, n, 1 - Termination set MX2: Node 2, 57600, 8, n, 1 - Termination set (this is the test setup. Eventually there will be more drives attached to the system hence the need for RS485) Quote Link to comment Share on other sites More sharing options...