Hello everyone,
I am come back to the forum since too much time. I come back to Unitronics' PLC programming and I have got an issue with a routine.
I am currently working with a generator routine which looks like:
We have a panel with 9 bottons to select a state for each generator (Day, Night, Standby). Therefore we have 6 combinations:
  1. Day,Night,Standby
  2. Night,Day,Standby
  3. Standby,Day,Night
  4. Standby,Night,Day
  5. Day,Standby,Night
  6. Night,Standby,Day
And if it is not any of these ones,it will work with this state like standard one: ''Day,Night,Standby"
Now the problems come. Time functions:
Day-07:00-19:00
Night-19:00-07:00
Standby should work when there is a failure in one of the other ones.
I made a simple visual checker with 3 pictures simulating the state of the generators, but I do not know why routines Gen1,Gen2 and Gen3 are always "ON".
I have attached the file in this link.
Thanks for your help.
When MB20 turns off, you stop calling "StandardRoutine". When you stop calling Standard Routine, you stop calling "Gen1" routine. When you stop calling Gen1 routine, the PLC cannot turn off MB17, thus it stays on.
Even if MB20 stays on, when the time expires in StandardRoutine, ladder rung 1, then Gen1 subroutine is no longer being called and MB17 cannot be turned off.
Conditional subroutine calls can be very problematic. Design your logic to minimize (or eliminate) the need for conditional subroutine calls.
Hi Sirs,
I rethink all the ladder logic, I would like to ask you if you notice at first look anything wrong, with ladder logic's LOGIC
I have the next pieces working. I am going to start working with a normal routine(Basic), generator 1 Day, generator 2 Night, generator 3 Standby and a transformer which is the main one.
I am simulating this program with bits instead with inputs and outputs.
I have the next componets:
Generator 1 start is MB5
Generator 2 start is MB6
Generator 3 start is MB7
Phase failure rele transformer is MB0
Phase failure rele Gen 1 is MB10
Phase failure rele Gen 2 is MB11
Phase failure rele Gen 3 is MB12
Breaker Switch Transformer is MB1
Breaker Switch Gen1 is MB2
Breaker Switch Gen2 is MB3
Breaker Switch Gen3 is MB4
Gen routine BIT MB8
PFR House  MB9
BUSBAR Alarm MB13
This is my program idea, I will performance and I will simulate. Could anyone say me if there is some confict condition with ladder logic in this program?
Thanks