I have an application where one Vision V130 PLC (Modbus master) reads over RS485 network 14 Jazz PLC –s (Modbus salves). Recently I add another 6 Jazz PLC-s to this RS485 network. The type of 14 old and four new PLC is JZ10-11T40 and other two new PLC –s are JZ20-R16. All Jazz PLC-s used MJ20-RS adapter. All termination resistors set up correctly (both ends ON, all others OFF). After all the installation and programming work was done, there are strange behavior with some new PLC –s.

Master PLC V130 can read all  JZ10-11T40 type PLC-s but if it start reading JZ20-R16 type PLC –s then port settings of that PLC –s goes to default values and  master can’t connect with them. Sometimes it happen immediately after restart (initializing correct port settings) and sometimes master can read slave during minute or two before

port settings changes their default values. Port settings I use: baud rate 9600, data bits 8, stop bits 2,  parity no, HW flow control none, timeout 1s.

 

What can cause that kind of malfunction?

  • 3 weeks later...
  • MVP 2023
Posted

Hi mkc,

Without knowing Jazz too much, only M91s, 2 comments:

1).  Why 2 stop bits instead of the standard 1?

2).  Given that the problem plcs are the new ones, perhaps you should use Controller/Operating System to check that all the Jazz's are using the same OS.  If the newer ones are a later OS, that might be the issue.  If they are, the easiest solution might be to match their OS to the older ones, rather than changing ALL of the oldies to new.

cheers, Aus

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.