alexmoskos Posted February 23, 2017 Report Share Posted February 23, 2017 Hi, I already have a couple of PT1000 temperature sensors that I would like to use with the expansion module UIS-WCB1 but the specification says it can only work with PT100 (and other thermocouples) but not PT1000. The temperature range this sensor will ever see is between 0-100 C. Because of this relatively smaller temperature range, would I be able to use the PT1000 sensor with this I/O module, by writing some code to account for the difference, instead of having to purchase the UIS-04PTKN module? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted February 24, 2017 MVP 2022 Report Share Posted February 24, 2017 Look at these resistance tables- 100 ohm RTD http://www.pyromation.com/Downloads/Data/385_c.pdf You'll note the highest reading is 390 ohms at 850 C 1000 ohm RTD http://www.thermometricscorp.com/PDFs/Platinum-1000-Ohm-385.pdf All the values are increased by a factor of 10. A 100 ohm input will totally barf if you connect a 1000 ohm load to it. Joe T. 2 Quote Link to comment Share on other sites More sharing options...