Looking for help getting my Samba SM70-J-TA22 to read my MKS 925 micropirani vacuum gauge on the 0-10VDC analog input. I have ML0 as my Analog IN and I'm reading values of 860 @ 1 volt and 1500 @ 9 volts. I need to linearize those values to 1E-5 and 1E3 respectively(chart below). Its a logarithmic scale so I'm not sure how to approach this. I know I need a MF as the pressure values have a decimal. Any guidance would be huge.

 

Chart.png.c5696680f17a6a50267b3daf120b2f51.png

Link to comment
Share on other sites

  • MVP 2023

You've probably already deduced that a regular linear block can't handle this.  

You're going to have to go into floating point land.  Convert ML 0 into a float an look at the functions available under Math->Float.  To see how to convert it, search "float" in the Help and choose Float:Convert.  Read the other Float topics while you're in there.

Here's a page I found that may have the formula you need:

http://stackoverflow.com/questions/19472747/convert-linear-scale-to-logarithmic

Google is your friend if you need more insight on the math.  It's been 30 years since I exercised the top buttons on my calculator.

Have a go at it and post what code you come up with if you need more help.

Joe T.

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...