Read values from Thermocouple J type in Samba 4.3"


Recommended Posts

Hello, I am new in all of this PLC field but I want to start with small projects in order to get some experience and then moving on bigger projects.

I want to put a graph in my HMI (I actually did it a  Variable thermometer Graph MI 12) and see the real temperature value over the graph. According to the Analog Input Wiring, I know that my input (9) AN0 and input (10) AN1 are the inputs.  First question: When I start to wire up. Do I just put a wire in AN0 and the other in AN1???? or should be connecting in parallel with V
+ one side and the other side with 0 -  references?????

And I know that I have to configure this inputs in my HW configuration. in Analog input I put:         No.     Type           Filter         Mode          Op       Addr         Description

                                                                                                                                                                                                                        0        0-10V        No filter                          MI         4                Thermocouple wire +

                                                                                                                                                                                                                        1        0-10 V      No filter                           MI         5                Thermocouple wire -

                                                                                                                                                                                                                      Can you guys check if this configuration is Ok? I appreciate the help!!!! I am not sure if I have to                                                                                                                                                                                                                                       link this with MI 4 or MI 5 with the thermometer graph above???

The last question is Do I have to Linearization in my ladder in order to scale values?   if Yes, which variable Do I have to attach the linearization?????

 

Thanks a lot 

sorry for mistakes my English is not my first language.

 

Link to comment
Share on other sites

What model SAMBA  are you using.  The   -T20 and  -R20 models do not support Thermocouples.

Thermocouples produce very small voltages in relation to the temperature being measured. The 0-10V Analog inputs ( 10 Bit )

are  not fine enough to read the millivolts generated.

Thermocouples are supported on the -RA22  and -TA22  Models.   The Installation Sheet  describes the wiring for the various types.

In the  -RA22 and  -TA22  thermocouple inputs is already  converted and the value  is stored as    xxx.x  degrees  C  or F

 

Link to comment
Share on other sites

The Samba is non-expandable so it is not possible to add the required thermocouple input(s) to the unit you have.   As Dan stated you'd have to look at the -RA22 or -TA22 models.

or you'd need an external module to convert the thermocouple input to a 4-20 or 0-10V signal that the PLC can accept.   Phoenix Contact or Weidmuller are two companies which have this type of module.

  • Upvote 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...