Hi,

I am trying to wire a 2 wire 0/4-20 mA analog output Flow Meter to a UIA-0204N I/O module, but It doesn't seem I get the correct reading.

The output of the sensor is active. From this I understand that I don't need to supply any DC voltage to the two wires of the sensor, thus one goes to 0V and the other to the input of my card. I also have 0V for the common on my card.

  • Do I also need to include a resistor between the wires of the sensor?

Also, being an active output from the sensor the card needs to act like a current sink.

  • How is that achieved? 

One last thing:

  • how can I easily determine if its 0-20 mA or 4-20 mA if it doesn't clearly specify it on the datasheet of the sensor?

Thanks

Link to comment
Share on other sites

Hi Sanyc

If it is an active transmitter then the transmitter has a separate power input.

Make sure the 0v of the transmitter power supply is linked to 0v of the unitronics input.

you should not put a resistor across the wires.

If you still have trouble please post a sketch of your wiring and the transmitter details.

Regards

Denis

 

Link to comment
Share on other sites

11 hours ago, sgull said:

If it is an active transmitter then the transmitter has a separate power input.

Make sure the 0v of the transmitter power supply is linked to 0v of the unitronics input.

Thanks Denis,

Indeed the transmitter has a separate 230V AC power supply. 

The common on my expansion module is connected to the 0V DC.

Then a wire from the (-) of the transmitter goes to the current input on the 0204n card.

The positive from the transmitter I 've tried both connected to the (+) and the (-) of the 24V DC supply with no success.  

Attached is a photo showing what I did

 

unnamed.jpg

Link to comment
Share on other sites

Hi Sanyc

From the document it says that the output can be passive or active.

If it is passive the output is 4-20ma and you should connect the positive of your 24v supply to the + of the instrument (terminal 26) and the - of the instrument (terminal 27) should go to the input of you analog input card.

If you select active than the - of the transmitter (terminal 27) is wired to the 0 common of the analog input and the + of the instrument (terminal 26) is wired to the input of the analog card. in this case you can select 0-20 or 4-20ma.

Regards

Denis

 

Link to comment
Share on other sites

Thanks everyone, problem solved and I am now reading very good values.

The problem turned out to be in the linearization, I set my Y limits to Y1 = 0 and Y2 = 18000, because I read in the manual that at 1'' the Flow Meter could read up to 18000 kg/h.

Eventually I scrolled the screen inside the Meter and found out that at 20 mA it gives maximum 6000 kg/h. 

So setting the linearization to Y1 = 1 and Y2 = 6000 solved the problem.

Thanks again

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...