Hi,

I am trying to wire a 2 wire 0/4-20 mA analog output Flow Meter to a UIA-0204N I/O module, but It doesn't seem I get the correct reading.

The output of the sensor is active. From this I understand that I don't need to supply any DC voltage to the two wires of the sensor, thus one goes to 0V and the other to the input of my card. I also have 0V for the common on my card.

  • Do I also need to include a resistor between the wires of the sensor?

Also, being an active output from the sensor the card needs to act like a current sink.

  • How is that achieved? 

One last thing:

  • how can I easily determine if its 0-20 mA or 4-20 mA if it doesn't clearly specify it on the datasheet of the sensor?

Thanks

Posted

I figured the last question; whether its 0-20 mA or 4-20 mA I can measure the current without any flow to determine the value of current so for a 4-20 mA without flow I should get 4 mA. 

Posted

Hi Sanyc

If it is an active transmitter then the transmitter has a separate power input.

Make sure the 0v of the transmitter power supply is linked to 0v of the unitronics input.

you should not put a resistor across the wires.

If you still have trouble please post a sketch of your wiring and the transmitter details.

Regards

Denis

 

Posted
11 hours ago, sgull said:

If it is an active transmitter then the transmitter has a separate power input.

Make sure the 0v of the transmitter power supply is linked to 0v of the unitronics input.

Thanks Denis,

Indeed the transmitter has a separate 230V AC power supply. 

The common on my expansion module is connected to the 0V DC.

Then a wire from the (-) of the transmitter goes to the current input on the 0204n card.

The positive from the transmitter I 've tried both connected to the (+) and the (-) of the 24V DC supply with no success.  

Attached is a photo showing what I did

 

unnamed.jpg

Posted

The transmitter is a Promass F80 Flow Meter. I also have the manual for it. 

Attached is a picture showing its output signals. My model is the one designated as HART

F80_Screeenshot.PNG

Posted

Hi Sanyc

From the document it says that the output can be passive or active.

If it is passive the output is 4-20ma and you should connect the positive of your 24v supply to the + of the instrument (terminal 26) and the - of the instrument (terminal 27) should go to the input of you analog input card.

If you select active than the - of the transmitter (terminal 27) is wired to the 0 common of the analog input and the + of the instrument (terminal 26) is wired to the input of the analog card. in this case you can select 0-20 or 4-20ma.

Regards

Denis

 

Posted

Thanks everyone, problem solved and I am now reading very good values.

The problem turned out to be in the linearization, I set my Y limits to Y1 = 0 and Y2 = 18000, because I read in the manual that at 1'' the Flow Meter could read up to 18000 kg/h.

Eventually I scrolled the screen inside the Meter and found out that at 20 mA it gives maximum 6000 kg/h. 

So setting the linearization to Y1 = 1 and Y2 = 6000 solved the problem.

Thanks again

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.