Hi everyone

I have HMI USP-070-B10 and need to connect to EX-RC1

I have done all in my project according to manuals but not transfer

Than I have loaded example EX-RC1_IO to Unistream and to EX-rc1 and again no transfer

 

I see that the HMI sends data and Alive data , but receive nothing

The same in EX-rc1 - send data and alive , but receive nothing

I have checked the wiring and power suply - all is ok

any idea where is the problem

Link to comment
Share on other sites

Hi  Oobretenov;

 

YOU MUST use the EX-RC1_IO.vlp example as your base program  from  the UniStream Examples because there are differences in

   MI registers being used   from the EX-RC1 Examples in Visilogic.

     Rename the file when you have made configuration changes to suit your project.

Did you  configure the EX-RC1 _IO   for your I/O Modules?

Set the DIP Switches on the EX-RC1 Module  for the address ( 2  and above)   UniStream is at Address 1  by default

Then do the Export file, and Import it into UniLogic.    The Export file from the EX-RC1  tells UniStream what I/O Modules are connected.

Make sure the   ID number you set is the same as the DIP Switch setting on the EX-RC1,  Leave the General Buffers  Unchecked.

Then do the  the Export from UniLogic of the INPUT and OUTPUT files-- At the top of the properties --, and Import these back into the EX-RC1.

      The Export files FROM the UniStream back to the EX-RC1  set up the Structs for the Inputs and Outputs properly

         to synchronize with the I/O Structs in  UniLogic.  Be sure to put the files in the right Structs  in the EX-RC1.

Be sure to Setup CANBUS  Com Parameters in BOTH the EX-RC1  and the UniStream to be the same Baud rate !  This is a separate setting in UniLogic.

Be sure the Terminating Resistors ( 75 ohm)  are on BOTH the UniStream Connect   AND the EX-RC1  Connector

The CANBUS is an   isolated  Communications system, It needs its own 24 VDC  power. It does not draw power from the EX-RC1 Module.

On the EX-RC1,  The  I/O COM  Led is Green and Steady when the I/O Modules are running properly.

 On the EX-RC1, The  BUS Com  LED  is on Steady when the CANBUS is communicating properly, else it flashes.

 

Dant

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...