Scholex Posted July 29, 2017 Report Share Posted July 29, 2017 es posible controlar un variador siemens utilizando el protocolo modbus RTU y unitronics JAZZ?? Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted July 30, 2017 MVP 2023 Report Share Posted July 30, 2017 Yes. If you haven't already, download the U90 software and search the Help for "Modbus". One thing to consider - you will need to add the RS232/485 COM port module. The added cost of this module puts the total cost of the Jazz close to the price of a V130, which has a COM port built in and a lot more power than a Jazz. Joe T. Link to comment Share on other sites More sharing options...
Scholex Posted August 2, 2017 Author Report Share Posted August 2, 2017 necesito leer la dirección 40111 de un variador G120 siemens utilizando un JAZZ con u modulo JZ-RS4, como puedo leer la dirección 40111 ya que solo puedo escribir en el bloque 4011?? Link to comment Share on other sites More sharing options...
MVP 2023 Joe Tauser Posted August 2, 2017 MVP 2023 Report Share Posted August 2, 2017 Modbus holding registers are indicated by the prefix "4", but it is not used in the actual address. Store "111" into SI 142. Joe T. Link to comment Share on other sites More sharing options...