Hi All,

I'm a new user of the Unitronics products.

I've a Visio V570 with the snap in V200-E18 E2B, now on my application I'm using the two analog inputs set as  4-20mA.

I'd like to know how detect a possible fail in the analog channel (for example the wire braking.....)

There is some ways to do this? I think to find for example in the system bit or system word some error code or alarm bit concerning a problem in the anolg input but I did not find anything.

Maybe I tried bad......

Thanks a lot for any suggestion.

Cheers

PB

 

Link to comment
Share on other sites

  • MVP 2022

Fail detection is inherent to 4-20mA. When the input sensor is at minimum value, you should see 4mA. If there is a fault (broken wire, broken sensor, etc), you should see 0 mA. Your V200-18-E2B module has 10-bit resolution, so you should see a value between 204 and 1023 in the MI assigned to the analog input. In your ladder code, just look for a value that is outside of that range to trigger your fault detection action. I would give it a little margin for error (maybe 190-1030) and also include a short timer to avoid false positives.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...