Thomasbe Posted May 25, 2018 Report Share Posted May 25, 2018 So i have a customer that want to expand some of their existing sites with more IO and the posibility to operate everything from two locations. There is already a vision 1210 on site. Is there an easy way to add a mirrored plc (as screen only) on the new location and expand with more IO ? (need to be able to operate everything from either of the locations. they are 100m apart) Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted May 25, 2018 MVP 2022 Report Share Posted May 25, 2018 Hi Thomas, There is no way to do a simple mirror. However, my interpretation of your ask is that the extra IO is being added to the 1210 that is already there. In that case, you could consider running Remote Access or Remote Operator via a dedicated mini puter and touch screen, linked to the existing 1210. (Various methods of the connection available) This would/should give you all that you want, and would likely be cheaper anyway. cheers, Aus Quote Link to comment Share on other sites More sharing options...
Thomasbe Posted May 28, 2018 Author Report Share Posted May 28, 2018 Thanks alot for the response! Do you know of any industrial grade touchscreen solution that can be mounted in a door front of a fusebox that can run Remote Operator? Im tempted to recommend upgrading to unistream series just to use VNC server/client solution. To expand the IO to the new location I just need an endblock and IO expantation block I assume? Again thanks alot! Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted May 28, 2018 MVP 2022 Report Share Posted May 28, 2018 I tried setting up a mirrored PLC a few years back. Since there are two active brains, data synchronization was an absolute nightmare. I would not recommend it. Your Remote Operator idea is probably the simplest solution. If you were starting from scratch a UniStream would be the way to go, but that's a lot of money and effort just to get a remote screen. As far as an industrial grade touchscreen, your choices are going to be somewhat dictated by your location. What country are you in? If the additional I/O is local to the V1210 then all you need is an EX-A2X and whatever modules. Ask your friendly local distributor to help. If the I/O is remote from the V1210 then you will need to set up a CANbus drop. Joe T. Quote Link to comment Share on other sites More sharing options...
Thomasbe Posted May 29, 2018 Author Report Share Posted May 29, 2018 Im located in Norway. I was thinking an android touchscreen to mount in the front door, but im guessing its hard to find something that wont break under pressure. This will be mounted under deck of a ship so it needs to handle a bit of vibration. Its remote IO so need the CANbus drop. Hope the distance wont cause any trouble. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted May 29, 2018 MVP 2022 Report Share Posted May 29, 2018 Google "marine panel mounted pc". If it's in a boat they don't get to tell you anything is too expensive, because as soon your money-saving idea breaks in rough seas they'll be crawling down your throat. I did find a panel mounted Android, but I've never used one. Look hard at the vibration spec. I sold some contactors to a military contractor years ago and then caught holy hell because they didn't hold up. They didn't tell me it was for a panel on a vehicle-mounted generator panel. Joe T. Quote Link to comment Share on other sites More sharing options...
Thomasbe Posted November 15, 2018 Author Report Share Posted November 15, 2018 Totally forgot about his thread. I solved it by setting up Master/Slave with their own IO in two locations over modbus. Having master PLC reading and writing raw values of IO every 0.5s. Then setting up password on both the display and locking the other so only one can be edited at any given time. This way both of the plc's can control the whole process with only 1s delay on each of them. WORKS GREAT! added a picture of it. Sorry for the Norwegian notes Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted November 15, 2018 MVP 2022 Report Share Posted November 15, 2018 Nice. Any reason you're running it so slow? If it's a direct wired Ethernet connection, you should be able to run at least 10 times faster, or more. I would be using SB 7 instead of SB 3. Quote Link to comment Share on other sites More sharing options...
Thomasbe Posted November 26, 2018 Author Report Share Posted November 26, 2018 I tried running it faster but it didnt tranfer all of the data when I did, so had to slow it down. Not sure why. Here is some of the data that is being tranfered all the time. Yes its ethernet wired between the two PLCs aprox 50 meters in a really hot engine room, and before you ask Cat 6 shielded to ground in one end. Quote Link to comment Share on other sites More sharing options...
Isakovic Posted November 26, 2018 Report Share Posted November 26, 2018 You ain't using "Function in Progress" bit before Modbus command. I can't see the rest of the logic, maybe you took it into account. But if you didn't, that may be the reason why it drops messages when you go faster. Quote Link to comment Share on other sites More sharing options...
Thomasbe Posted November 27, 2018 Author Report Share Posted November 27, 2018 MB 84 on picture. Its not really a problem since its working on multiple ships, but just out of curiosity I'd like to figure out why its not working when I speed it up. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted November 27, 2018 MVP 2022 Report Share Posted November 27, 2018 You need the "Function in Progress" bit before the MODBUS R/W function also. Quote Link to comment Share on other sites More sharing options...