Having an issue getting 4-20mA sensors to read on a V350-35-r34.


Recommended Posts

So after a lot of troubleshooting I'm officially out of ideas, so hopefully someone can see what I'm missing. My current set up is 2 4-20mA pressure sensors hooked up to the 2 analog inputs on the V350-35-r34. Wiring is + to PLC input, - to power supply 0v which is commoned with the PLC, ground to ground. The jumper setup is A A B B B from 1-5, so just the analog jumpers changed over.

I have tested literally every aspect of this setup, both sensors are a complete loop when tested, the PLC reads correctly if I use a 4-20mA loop simulator, all the wires are intact, I've tested it at the minimum distance of the wires, I've used 2 different PLCs, I've quadruple checked the program and all of that setup. I have literally no idea what is wrong at this point. Is there anything else anyone can think of to test or troubleshoot with this?

Link to comment
Share on other sites

  • MVP 2023

If your transmitters are two wire devices (loop powered) you have to hook + of the transmitter to +24V, - of the transmitter to the + PLC inputs.

All that's connected to the + PLC input is a resistor to COM.  Your transmitter provides the current that then provides a voltage to the PLC's A/D converter.

Joe T.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...