Dayglow Posted October 11, 2018 Report Posted October 11, 2018 I have a Jazz JZ20-T40 that I wrote a program for and am attempting to check the logic. I download the program and enter debugging mode. I wrote in SBs for HMI buttons to check the outputs which work fine. However, when I give the inputs 24 VDC with a wire to check them, they stay at 0 on the inputs screen. Shouldn't the inputs change to 1 when given 24 VDC? How should I go about checking my input logic on Jazz PLC?
Dayglow Posted October 11, 2018 Author Report Posted October 11, 2018 Solved. I didn't have pins 3 and 4 grounded to set the input to PNP.
MVP 2023 Ausman Posted October 11, 2018 MVP 2023 Report Posted October 11, 2018 Those darn input settings rearing their ugly heads again! ? ? cheers and well done, Aus