Guest Gennady Kozyukin Posted November 28, 2018 Report Share Posted November 28, 2018 Hello, In our laboratory we have xyz table for diode laser with v570 hmi controller. After the battery go dead, I have updated the firmware and uploaded the system file. Everything is ok, but the X and Y axis display negative values after the homming. How could I fix it? I uploaded vlp file to Gdrive. Thanks. Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted November 28, 2018 MVP 2022 Report Share Posted November 28, 2018 I have put the file directly here for everyone's convenience. More soon. cheers, Aus Laser Technion X Screw.vlp Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted November 28, 2018 MVP 2022 Report Share Posted November 28, 2018 This topic is doubled. Everyone please only respond on this one. Copy of Kratmel's answer from duplicate topic: Maybe min and max position in system parameters is wrong. Max is in min parameter and min is in max. cheers, Aus Quote Link to comment Share on other sites More sharing options...
MVP 2022 Ausman Posted November 28, 2018 MVP 2022 Report Share Posted November 28, 2018 A quick look appears to show MB114 linked to a "Zero Spindel" and a touch button that appears to be Bottom Right/Speendell Operation. Maybe pursue this a little? I can't read a lot of the screens, and assume it is a language issue. cheers, Aus Quote Link to comment Share on other sites More sharing options...