ietmn Posted April 28, 2011 Report Share Posted April 28, 2011 Hey! I'm trying to upload a project from a V280 plc. Everything seems fine while establishing communication between the PLC and the pc, I start to upload and it goes ok, but when the process gets up to 85% it stops and generates an error, the attachment shows what it is. I connect to it by a usb-serial converter (RS232). I'd appreciate your help!! Quote Link to comment Share on other sites More sharing options...
Ofir Posted May 2, 2011 Report Share Posted May 2, 2011 Hi, Which OS installed on the V280? Using which VisiLogic version the program was downloaded to the PLC? Try uploading the application using the same Visilogic version. You can try also uploading using different PC. Another try will be to download the latest VisiLogic version 9.2.0 and try uploading again. Quote Link to comment Share on other sites More sharing options...
MVP 2014 Simon Posted May 5, 2011 MVP 2014 Report Share Posted May 5, 2011 Just a simple check, make sure you are using 57,600baud or lower. Newer versions of Visilogic will default to 115,200baud. The V280 will start to communicate at that speed, but will lose the plot at some point. Quote Link to comment Share on other sites More sharing options...