Dah Posted March 10, 2019 Report Posted March 10, 2019 Hi Communication Driver Error (206). I changed the cable, changed the computer, COM port number, baud rate and nothing, my operating system is in windows 10, don't know if its windows 10 problem, Someone could help me? I don't know what to do anymore. Thanks
MVP 2023 Flex727 Posted March 10, 2019 MVP 2023 Report Posted March 10, 2019 We need to know which PLC, what version of VisiLogic, what communications method, and what physical connection you are using. It would also be helpful to know if you've tried other connection methods and if you were able to connect previously, and if so, what changed? Also, are you trying to connect to a new PLC or one that already has a project loaded?
Dah Posted March 10, 2019 Author Report Posted March 10, 2019 i am using a virtual PLC on my computer , the version of visilogic i am using is 9.8.78, i am tryig to connect to the virtual PLC Vision V130,
MVP 2023 Joe Tauser Posted March 10, 2019 MVP 2023 Report Posted March 10, 2019 1 hour ago, Dah said: virtual PLC Vision V130, Where did you get a virtual PLC? Joe T.
MVP 2023 Ausman Posted March 10, 2019 MVP 2023 Report Posted March 10, 2019 25 minutes ago, Joe Tauser said: Where did you get a virtual PLC? +1 to this. I'd like to know, too. Or do you think that because you have Visilogic working with what you set up as a V130, then this is your "virtual plc" and you can test it? cheers, Aus
MVP 2023 Ausman Posted March 12, 2019 MVP 2023 Report Posted March 12, 2019 Edited for clarity many minutes after posting. I don't fully understand the significance of your screenshot, except to say that the V130 window is what comes up when you try to use Remote Access, or actually get online with a physical unit and choose to display the HMI during that. But in the screenshot there are no power lines showing that you are online ok. What is the highlighted folder selection meant to represent? cheers, Aus
Gabriel Franco Posted March 12, 2019 Report Posted March 12, 2019 I guess you´re using Remote Access software to show your Vision 130 and you believe it is a simulator. However keep in mind that all Unitronics software requires a physical PLC in order to view online data. There is not simulator.
Dah Posted March 13, 2019 Author Report Posted March 13, 2019 I have a problem in serial physical communication as well as virtual communication i mean I can not communicate with the automaton I found 10 miles means that does not work anymore 😫
MVP 2023 Ausman Posted March 13, 2019 MVP 2023 Report Posted March 13, 2019 So you have a V130 10 miles away, and you want to connect to it? Is this what you are saying? I think this is just a translation issue, in that you are calling Remote Access your "virtual communication"? cheers, Aus
Jonattan GR Posted May 27, 2019 Report Posted May 27, 2019 On 3/10/2019 at 11:37 AM, Flex727 said: We need to know which PLC, what version of VisiLogic, what communications method, and what physical connection you are using. It would also be helpful to know if you've tried other connection methods and if you were able to connect previously, and if so, what changed? Also, are you trying to connect to a new PLC or one that already has a project loaded? Hello, I have a similar problem, I have a PLC V350-J-TR20, the Visilogic version is 9.8.79 Build 0 Beta, I have the RS232 physical connection with the MJ10-22-CS25 cable, the PLC already has a program loaded, the last program has a modbus configuration that is possibly causing me the error, what do you recommend doing? Thank you
DanT Posted May 28, 2019 Report Posted May 28, 2019 H; A few more questions : What is the Communications setup in the PLC ( V130, V350 )? Port 2 -- Ethernet or RS232/485 or None? Which Port is being used for Programming? Which Port is being used for Modbus? Is the Modbus Serial ( RTU) or Ethernet (TCP) ? What is the Baud Rate for the Com Port(s)? If unknown, this can be checked via Info Mode. Is the Modbus set up as Master - Doing the polling? or as Slave - Responding to requests for data? Are you using COM 1 for Modbus and Programming? Using COM1 as a Modbus Master and for Programming is asking for trouble Communications Clashing - In and Out Is there a way in the program to disable the Modbus Communication and allow the port to be used for programming ? Maybe in a user menu? Separate if at all possible - Add a 2nd Comport or Ethernet Port. If there is a COM 2 and it is RS232/485 then this would normally be used as the Modbus Com Port and Com 1 is open for Programming and Remote Access Is Com 2 Setup for Ethernet ? -- IP address and PLC Name and the Program Name can be gotten via Info Mode. Then Modbus Serial will use Com 1 , and you can get into the PLC via Ethernet You can go Online with the Unit and at least looks at the data even if you do not have the program. You can try an UPLOAD from the PLC - If the program is unlocked, you can recover the ladder. -- If the ladder is locked, then you are out of luck. ( DO NOT ATTEMPT a DOWNLOAD as this will overwrite the program in the PLC !!!!!! ) DanT
Jonattan GR Posted June 11, 2019 Report Posted June 11, 2019 On 5/28/2019 at 8:18 AM, DanT said: H; A few more questions : What is the Communications setup in the PLC ( V130, V350 )? Port 2 -- Ethernet or RS232/485 or None? Which Port is being used for Programming? Which Port is being used for Modbus? Is the Modbus Serial ( RTU) or Ethernet (TCP) ? What is the Baud Rate for the Com Port(s)? If unknown, this can be checked via Info Mode. Is the Modbus set up as Master - Doing the polling? or as Slave - Responding to requests for data? Are you using COM 1 for Modbus and Programming? Using COM1 as a Modbus Master and for Programming is asking for trouble Communications Clashing - In and Out Is there a way in the program to disable the Modbus Communication and allow the port to be used for programming ? Maybe in a user menu? Separate if at all possible - Add a 2nd Comport or Ethernet Port. If there is a COM 2 and it is RS232/485 then this would normally be used as the Modbus Com Port and Com 1 is open for Programming and Remote Access Is Com 2 Setup for Ethernet ? -- IP address and PLC Name and the Program Name can be gotten via Info Mode. Then Modbus Serial will use Com 1 , and you can get into the PLC via Ethernet You can go Online with the Unit and at least looks at the data even if you do not have the program. You can try an UPLOAD from the PLC - If the program is unlocked, you can recover the ladder. -- If the ladder is locked, then you are out of luck. ( DO NOT ATTEMPT a DOWNLOAD as this will overwrite the program in the PLC !!!!!! ) DanT V350, Port 2 Ethernet; I wa using RS232; I wanted to use port 1 for the modbus RTU, now I cant enter via RS232, Using COM1 as a Modbus Master and for Programming is asking for trouble Communications Clashing - In and Out...... Yes, It is just the problem that I have. I dont have problem to lose the PLC program Can I load a new program from the SD?
DanT Posted June 11, 2019 Report Posted June 11, 2019 Hi; Yes, the SD card can be used to download a new program into the PLC. In VisiLogic, Projects - Create the download file. Format the SD card using the SD Card Utilities - this also adds Unitronics specific folders onto the card. In the V350, use Info Mode and SD card Functions to install the new program. If the PLC has an Ethernet Port, you can also download thru the Ethernet Port ( IP and PLC Name are required) If No 2nd com port, create a service screen and disable the Modbus Activity while working thru COM1, then enable Modbus Activity when done. DanT
AlexUT Posted June 11, 2019 Report Posted June 11, 2019 Hi, I can add to what DanT say. Use the same VisiLogic you used to download project to PLC last time. This is important to have all system files compatible with used VisiLogic version. Only OS may be updated from SD card.
Tomo321 Posted July 23, 2020 Report Posted July 23, 2020 Hi, I have a similar problem with the PC-PLC connection. PC Win10 VisiLogic 9.8.91and PLC SAMBA SM35-J-R20. I connected many times modifying the plc program without problems. When I changed and uploaded the MODBUS connection data, an error 206 (communication driver error) appeared. Now I can't connect and change anything. The PLC only has a RS232 RJ11 port. I am using Unitronics RS232-CB1 cable. What should I do?
MVP 2023 Flex727 Posted July 23, 2020 MVP 2023 Report Posted July 23, 2020 56 minutes ago, Tomo321 said: When I changed and uploaded the MODBUS connection data What did you change? If you changed the comm settings for your serial port being used for PC-PLC comms, then you can interrupt the ability to connect from VisiLogic. Go into INFO Mode and check your serial port settings.
Tomo321 Posted July 23, 2020 Report Posted July 23, 2020 I did not change the communication settings. I just modified FB's MODBUS in Ladder and removed Direct Contact Power-up bit.
MVP 2023 Joe Tauser Posted July 23, 2020 MVP 2023 Report Posted July 23, 2020 Can you post your program? Joe T.
Tomo321 Posted July 23, 2020 Report Posted July 23, 2020 Yes, this is my program PROGRAM 2P 0161 GSM 3.vlp
MVP 2023 Joe Tauser Posted July 23, 2020 MVP 2023 Report Posted July 23, 2020 You're calling the COM INIT 1 continuously, which is stomping on your com port. You only need to call it once when the PLC boots. I added an SB 2 power-up bit on a contact to network 20 in front of the INIT and CONFIG instructions. You'll probably have to put your PLC in stop mode from the INFO mode screen to download this. If you don't know how to get into INFO mode, take a quick look at the Help for instructions and let us know if you have trouble. Joe T. PROGRAM2P0161GSM3 JT.vlp
Tomo321 Posted July 23, 2020 Report Posted July 23, 2020 Thanks a lot but i can't download the file. INFO MODE instruction is for Vision model but not SAMBA. I do not know how to do this
MVP 2014 Simon Posted July 23, 2020 MVP 2014 Report Posted July 23, 2020 Info mode in Samba is same as Vision models that are touch screen only (eg V570, V700). Hold your finger on the touchscreen, in an area where there are no active touch elements, and wait 5 seconds.
de003 Posted July 24, 2020 Report Posted July 24, 2020 Hi All. I have recently bought a Samba 35-J-R20 for a small project. I am new to Unitronics. I cannot get VisiLogic and the PLC to talk - I'm getting the same 206 comms error as above. This is in a new, blank file - just trying to get comms between VisiLogic and the PLC. I'm using a USB-DB9 RS232 adaptor, and a DB9-RJ11 cable jumper. In Device Manager, in VisiLogic, and on the PLC (Info Mode) I have the same comms settings - COM Port 1 (Serial), Baud rate 57600. It offers me four potential causes: 1. Cable connections not secure (checked - they are) 2. Timeout is too short - it's set to 1s... I tried it at 10s out of principle, and no change. 3. Incorrect communication settings (see above) 4. Current user name is not authorised for this action: I have not logged in to anything so I don't know where to check this... I haven't got the means at home to go testing cables. Can I just ask if I've forgotten to check anything simple before I start blaming hardware?
MVP 2023 Ausman Posted July 24, 2020 MVP 2023 Report Posted July 24, 2020 5 hours ago, de003 said: USB-DB9 RS232 adaptor, and a DB9-RJ11 What are these exactly? They are the likely cause of issues if not correct/good enough. cheers, Aus