V1210 Expansion Error 400


Recommended Posts

Hello,

I have a pannel V1210 with expansion modul EX-A2 connected to IO-AI4-AO2 (1 modul), IO-DI16A3-RO16(3 moduls), IO-RO16(2 moduls). The moduls that i worte are in this consequence. 

All moduls are not more than the maximum requirement, but after couple of minutes of being active a sign pops up saying "expansion error 400" and the CPU goes into stop being in avtive mode. 

The power supply is exactly 24VDC, we replaced couple of different cables connecting the CPU and EX-A2, all connections between the moduls are checked and working, so it is not the connecting cable. All the electrical connection is okay. 

Why does it say "expansion error 400" when we try to make it work? Where could be the problem in the system?

Link to comment
Share on other sites

  • 2 months later...

dear

I went through the same problem. In my case it was the interconnection cable between the EX-A2X module and the V1210. Before replacing the cable, I had to connect the RG pin (13) on the D16A3 card to the 0V pin on the 24V supply. I also recommend installing the analog inputs and outputs module at the end of the rack. Install the D16A3 modules right after the EX-A2X

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...