dierkens Posted May 1, 2020 Report Share Posted May 1, 2020 I'm working with OPC/UA right now and just to clarify a few things: 1) The existing help file [September, 2019] mention of the certificate in the PLC [UniApps->Network-> (2nd Page)-> OPCUA] may or may not be present in there. It depends on the OPC/UA Client program. 2) The generation of the OPC/UA certificate appears to be created/generated when the PLC is first powered up. In order to get the OPC/UA Client to connect I had to download the program and then reset/reboot the PLC. 3) If you plan to implement OPC/UA do yourself a favor and wrap all of your tags into one or more Structs. You can add Structs to the OPC/UA Address Space. Otherwise you have to add the tags one at a time. For my existing project that means adding 168 tags by hand. And of course I find it necessary to have the OPC tag name match that of the 'source' tag exactly. That means at least 600 actions to add them. [I batch process similar to that of the MODBUS configuration would come in handy. Hint Hint !!!]. If anyone has any additional tips/tricks/faqs please add them. 1 Quote Link to comment Share on other sites More sharing options...