LEONARDOJH Posted September 27, 2020 Report Share Posted September 27, 2020 buenas noches, tengo un problema tengo el V200-18-1B al en las salidas le conecto tal cual el plano del manual las entradas v0 y v1 a una fuente de 24vdc y le coloque un rele a la salida O0 y O1 y hice la conexion pero no tengo respuesta de la salida. medi continuidad entre O0 y N y tiene continuidad eso significa que la salida O0 es de contacto cerrado?? Quote Link to comment Share on other sites More sharing options...
AlexUT Posted September 27, 2020 Report Share Posted September 27, 2020 Hi, All outputs are Normal Open. Power-off PLC. If contact stay closed, then contact is welded. Quote Link to comment Share on other sites More sharing options...