vken Posted October 2, 2020 Report Share Posted October 2, 2020 Hello , I 've got an Energy meter (yes again!) which returns 16bit registers at the maximum range 65535. some times that is also negative... that is format IEEE 754 It's the first time see this format and I can't find a way to read automatically the correct values. I read some articles and some other post with multi array but this is not multiarray it's just a number which need some calculations on it if I got it right? (find the "mantissa" and so on). Or I got it totally wrong ... any Ideas ? thank you p.s I 'm using a US5-B10-TR22 Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted October 3, 2020 MVP 2022 Report Share Posted October 3, 2020 I looked up IEEE 754 regarding Modbus and it seems that it's a standard floating point format, which is 32 bits. Have you tried reading it into a REAL data type? Joe T. Quote Link to comment Share on other sites More sharing options...
vken Posted October 3, 2020 Author Report Share Posted October 3, 2020 Hi Joe, yes I did, I also checked two other post from the forum. 1. 2. but as far I can understand is that the reading should be in two arrays or two registers. how ever I was not able to read two arrays from unistream. according to the energy meter's manual they are 4 bytes (2 registers) per parameter. http://support.innon.com/PowerMeters/SDM630-MOD-MID/Manual/SDM630-Modbus_Protocol.pdf if I connect with an adapter to the energy meter with modscan64 I can read the values also in float format When is saying 4 bytes (2 registers) they are 2 registers in row? for example 30001 and 30002 ? p.s I'm beginner in Modbus but I think not that bad Quote Link to comment Share on other sites More sharing options...
ORSO2001 Posted October 3, 2020 Report Share Posted October 3, 2020 Just to know...are you trying to read info starting from address 1 or address 0? because the column called "Modbus Protocol Start Address Hex" show that you have to start from address 0x0000...then 0x0000 and 0x0001 will contain the info about the "Phase 1 line to neutral volts"; address 0x0002 and 0x0003 will contain ythe info of "Phase 2 line to neutral volts"...and so on Quote Link to comment Share on other sites More sharing options...
Isakovic Posted October 3, 2020 Report Share Posted October 3, 2020 The way that Sargani explained in post number 2 should work. 6 hours ago, vken said: but as far I can understand is that the reading should be in two arrays or two registers. how ever I was not able to read two arrays from unistream. 6 hours ago, vken said: When is saying 4 bytes (2 registers) they are 2 registers in row? Yes you can (and should in this case) read several registers in a row. If in "Modbus Master" setup you define tag as an array of 16 bit integers, let's say of length 10, PLC will read 10 consecutive registers from Modbus Slave. Can you post part of the program with code for making 32 bit float from 16 bit ints, with setup for Modbus so we can help you find the problem? Quote Link to comment Share on other sites More sharing options...
vken Posted October 4, 2020 Author Report Share Posted October 4, 2020 Hi, thank you both! So that's why I need a Gurus to guide me ORSO you are right that I miss that point and Isakovic stretch me to the reading of several registers in row. I made some test, here is the code but still don't have the correct result. correct me if I'm wrong: 0x12345678 Reg 0 - Hi is 34 | Reg 0 - Lo is 12 | Reg 1- Hi is 78 | Reg 1 - Lo is 56 the format in order to be read as float should be 34,12,78,56 ? what I tried to do in the attached is that but is not working they are 2 lines here, one with Sargani's explanation that looks pretty nice and give in "Buffer 1" the above format, but I'm still missing something to have the right result the second is a deferent approach but also half and far way. thank you for you patience. US5_B10_TR22 - Copy.ulpr Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted October 4, 2020 MVP 2022 Report Share Posted October 4, 2020 I thought this sounded familiar. Your Modbus words probably need to be swapped to have the correct value. Notice I said WORDS, not bytes. Keep in mind that Buffer data types are 8 bits (bytes), while Modbus returns registers in 16 bit words. This is VERY IMPORTANT - have you been able to actually read a value from your meter? What is that value? Do you know what the corresponding floating point value is? 9 hours ago, vken said: I made some test, here is the code but still don't have the correct result. correct me if I'm wrong: 0x12345678 Reg 0 - Hi is 34 | Reg 0 - Lo is 12 | Reg 1- Hi is 78 | Reg 1 - Lo is 56 the format in order to be read as float should be 34,12,78,56 ? what I tried to do in the attached is that but is not working There is no right answer to this. I know you're trying very hard to get a firm definition, but the byte and word order on a floating point number varies from manufacturer to manufacturer. When Modbus was created floating point numbers weren't something that was thrown around so its format was not defined. This has led to much confusion in today's world where young device programmers always put data in floating point format but do not try to adhere to a standard. You MUST have an actual word from your device and it's corresponding floating point value to decode. Here's a post of mine from June 6, 2019. You mentioned this thread in one of your earlier posts but I don't think you followed this through. As you've already done, read the data from the device into a UINT32 tag. For testing I made one called "Read Data" that I could simulate, and a tag called "Conv Value" to hold the swapped bytes. The data will land in a REAL called "Converted". In UniStreamSpeak- 1. Copy the data you read from the device to the working tag and Swap the bytes using "Logic->Swap Single Tag Bytes" with Swap Type.ABCD_CDAB. 2. Copy the swapped data to a 4 byte BUFFER array type so you can manipulate the memory directly. Mine is "Conv Buffer[4]". 3. Use "Buffer Tools->Copy Tag to Buffer" to get the "Conv Value" data into the buffer tag and "Copy Buffer to Tag" to get it from the buffer to the REAL "Converted". There you go. Sorry it doesn't have all the digits you're looking for. If you need to convert several values write a UDFB to move the data into this logic with a pointer. Quote Link to comment Share on other sites More sharing options...
vken Posted October 5, 2020 Author Report Share Posted October 5, 2020 Hi Joe, thank you for your msg. I'll connect it again to the modscan64 to identify the words... from there I can swap in real time from HEX to Bit and so on.... ... regarding the example you attached is something that i tried but I 'll tried it harder! Quote Link to comment Share on other sites More sharing options...
vken Posted October 6, 2020 Author Report Share Posted October 6, 2020 I want to give a feedback and some more info because I found it difficulty .... well it looks that it works! the "words" reading is easier and clear approach. I don't have clear reading about Voltage of Phase 1, some times is around 230xxxxx... but most of the time is like 59139010000000000000000000.000000 but it's a stable reading. for Hz the reading is clear for both of them I can't find a way to move the decimal point. for example to have 49.84 Hz instead of 49837.520000 any idea how to manage the length of the values US5_B10_TR22 - v3.ulpr Quote Link to comment Share on other sites More sharing options...
ORSO2001 Posted October 8, 2020 Report Share Posted October 8, 2020 hi vken, from your picture I saw that the function 1 (maybe is the main function) has no BIT trigger to do the conversion from 2xint16 and REAL...also to perform the byte swapping...so this funciton will called a many times (one for each PLC cycle)...please try to insert a BIT command to perform these actions. regards Quote Link to comment Share on other sites More sharing options...
vken Posted October 9, 2020 Author Report Share Posted October 9, 2020 Is it necessary when you set the modbus in unistream like here? Quote Link to comment Share on other sites More sharing options...
MVP 2022 Flex727 Posted October 9, 2020 MVP 2022 Report Share Posted October 9, 2020 On 10/6/2020 at 1:44 PM, vken said: I I am, frankly, shocked that this works. Each of those rungs should be broken up into at least two, if not three rungs. I can't believe that "Buffer 1" or "Buffer 2" has completed both parts of the Copy Tag operation before the Copy Buffer occurs. Quote Link to comment Share on other sites More sharing options...