m_a_s001 Posted October 9, 2020 Report Share Posted October 9, 2020 Hello everybody! Please I need some help! I´m trying to command a G120 with a V350 via modbus (over Rs485 - two wires). The communication its ok, but I can´t change to Run status the inverter. The Starter display the following: My program is the following First: I write 0x47E in the parameter 40100 Seond: I write the Main Set point in the parameter 40101 Third: I write the command 0x47F in the parameter 40100 if someone can send me an example or give me some help, I will be very grateful!! Thanks a lot!! Mario Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted October 10, 2020 MVP 2022 Report Share Posted October 10, 2020 Hi, Some quastions: 1) Is it speed and 8E1 (simens default) settings commisioned corectly in V350 com settings? 2) Is it G120 setpoint channel sw. = Modbus, Control channel = Modbus? 3) Is it G120 correctly commisioned and all self autotune done and all autotune settings written to the drive . Drive do not allow to net control before autotune done (default). 4) What is with modbus status when command was send? maybe this document is useful: https://static1.squarespace.com/static/5357e4cfe4b02760ee8a9506/t/53ecf6f2e4b03c7a36fcfed3/1408038642976/MicroBridge+Modbus+Plus+to+G120+App+Note.pdf chapter Verifying the Installation Quote Link to comment Share on other sites More sharing options...
MVP 2022 Joe Tauser Posted October 11, 2020 MVP 2022 Report Share Posted October 11, 2020 Do you have the wired Enable signal on the drive terminals connected (DI0)? Joe T. Quote Link to comment Share on other sites More sharing options...
m_a_s001 Posted October 13, 2020 Author Report Share Posted October 13, 2020 On 10/10/2020 at 11:41 PM, Joe Tauser said: Do you have the wired Enable signal on the drive terminals connected (DI0)? Joe T. Hello Joe, DIO es connected to a sensor, The signal is ok I try with DI0 in ´1´ or ´0´ but the result is the same, the inverter is stopped. All the inputs have the right connection and I chek if the signals are OK. All is ok, but the problem persist.... 😞 Quote Link to comment Share on other sites More sharing options...
m_a_s001 Posted October 13, 2020 Author Report Share Posted October 13, 2020 On 10/10/2020 at 4:35 PM, kratmel said: Hi, Some quastions: 1) Is it speed and 8E1 (simens default) settings commisioned corectly in V350 com settings? 2) Is it G120 setpoint channel sw. = Modbus, Control channel = Modbus? 3) Is it G120 correctly commisioned and all self autotune done and all autotune settings written to the drive . Drive do not allow to net control before autotune done (default). 4) What is with modbus status when command was send? maybe this document is useful: https://static1.squarespace.com/static/5357e4cfe4b02760ee8a9506/t/53ecf6f2e4b03c7a36fcfed3/1408038642976/MicroBridge+Modbus+Plus+to+G120+App+Note.pdf chapter Verifying the Installation Hi!, First of all, thanks for your time!. I respond your questions: 1) Is it speed and 8E1 (simens default) settings commisioned corectly in V350 com settings? The comunication it´s ok because I can write and read diffents parameters (I set 8 bits, Even and 1 stop bit) 2) Is it G120 setpoint channel sw. = Modbus, Control channel = Modbus? I can´t find the control channel parameter. 3) Is it G120 correctly commisioned and all self autotune done and all autotune settings written to the drive . Drive do not allow to net control before autotune done (default). Autotune is done 4) What is with modbus status when command was send? The modbus Status is 0 (communication OK Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted October 13, 2020 MVP 2022 Report Share Posted October 13, 2020 Hi, in Verifying the Installation chapter of document in my above post present Modbus registers that can be sw. OFF1 bit directly. Please try to do this for test - it is the same idea as Joe provide with DI0 but via software. Quote Link to comment Share on other sites More sharing options...
m_a_s001 Posted October 15, 2020 Author Report Share Posted October 15, 2020 On 10/13/2020 at 3:30 PM, kratmel said: Hi, in Verifying the Installation chapter of document in my above post present Modbus registers that can be sw. OFF1 bit directly. Please try to do this for test - it is the same idea as Joe provide with DI0 but via software. Hello! I try set the parameter 40003 ( number 2 in visilogic) but the communication state change to "5". Another question, the "big endian" formtat, used by Siemens, could be the origin of the problem? Thanks for your time and help! Best regards Mario Quote Link to comment Share on other sites More sharing options...
m_a_s001 Posted October 16, 2020 Author Report Share Posted October 16, 2020 Hello People! I solved the problem!!!! It was a mistake in the stw confiuration, I correct this with the values of the manual: Thank you for your help and time! If in the future I can help with something, please count on me! Best Regards Mario Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted October 16, 2020 MVP 2022 Report Share Posted October 16, 2020 Great news. If it possible - please select by red ink parameters in table that you change for rectify problem. And this table can be useful for another forum users. Quote Link to comment Share on other sites More sharing options...
m_a_s001 Posted October 20, 2020 Author Report Share Posted October 20, 2020 On 10/16/2020 at 6:59 PM, kratmel said: Great news. If it possible - please select by red ink parameters in table that you change for rectify problem. And this table can be useful for another forum users. Hello, I can solve my problem setting the G120 parameteres like the information of the table (parameteres marked in yellow) Best regards! Mario 1 Quote Link to comment Share on other sites More sharing options...