hane6 Posted August 28, 2010 Report Share Posted August 28, 2010 way to maintain the last measured value before the break Quote Link to comment Share on other sites More sharing options...
Emil Posted August 29, 2010 Report Share Posted August 29, 2010 Hi Hanne6, Simple soluiton: 1. Each scan, out of Power up, store MI39 to any other, buffer MI, let say MI139. 2. On Power up, store back buffer value (MI139 in our example) back to MI39. You can use SB2 - power uop bit as condition to perform the mentioned logic. In point 1 - use N.C. contact. In point 2 - N.O. Quote Link to comment Share on other sites More sharing options...
hane6 Posted September 3, 2010 Author Report Share Posted September 3, 2010 Ok I forgot the important word in the title, "when the measurement wire is broken. etc." So, we have power on. Meassurement signal is 4...20 mA. So input value "204" means 4mA. Limit 170 can indicate, that there is a fault in measurement... Quote Link to comment Share on other sites More sharing options...