V570-57-T20B-J with V200-18-E1B Relay Outputs


Recommended Posts

qa.PNG.674f5e0b765e8b238004d4d96abe2115.PNGHello,

I'm using a V570-57-T20B-J with V200-18-E1B, I'm trying to turn on/off an LED (Binary Image) on my HMI with the use of a relay output.
I have powered my unit;
+V: 24V
0V: 0V,

and the relay output shown in the image below. I have also written a logic and linked in my HMI as shown below:
With the connections, the LED does not change to RED. Any help would be appreciated
 

 

1w2.PNG

Link to comment
Share on other sites

  • MVP 2023
2 hours ago, Khom said:

I'm trying to turn on/off an LED (Binary Image) on my HMI with the use of a relay output.

With what you have shown this sentence doesn't make sense.  You want to use a relay output, yet you are using an MB to trigger a screen element indirectly linked to the output.   So what is it that you want?  The screen element to concurrently change when the relay changes?  I guess this.  So the real question here is what controls your O 0?, because you've actually got that as a contact.  If something else is turning O 0 on, then simply link O 0 instead of MB24.

After all that, at present, does MB24 actually change when you think it should when online?

cheers, Aus

Link to comment
Share on other sites

Hi Khom

If you wire the PLC the way you have shown and output 0 comes on you will short out your 24v supply.

Do NOT connect  24v to one side of the output and 0v to the other (the output is just a switch)

As Aus asks, let us know exactly what you are trying to do.

To bring on the output you need some condition in the ladder to trigger output 0.

You are correct with linking the contact of the output to the MB to change the image on the display (you can also link direct to the output)

Regards

Denis

 

Link to comment
Share on other sites

  • MVP 2023

I think he's just got things wrong way around. @Khom, you need to check the box to the left of the word "Toggle", then link MB 24 to O 0 the reverse of the way you have it:

MB 24     O 0

---|  |------(  )-

 

Edit: Upon re-reading, I think you're using some other condition to activate MB 24 (some alarm condition), not trying to toggle it by touch on the screen. In that case, simply leave the Toggle box unchecked and the logic will work properly as long as you have a coil somewhere for MB 24 that is activated for your alarm condition.

Link to comment
Share on other sites

  • MVP 2014

Hi Khom,

It looks like you are treating th e relay output as if it were an input.  Try linking I0 (Input Zero) to the contact, and wire the inputs on the module accordingly. 

      I 0     MB 24

---|  |------(  )-

Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...

Important Information

This site uses cookies. By clicking I accept, you agree to their use.