Unistream CanOpen Problem


merttoprak

Recommended Posts

  • MVP 2022

Hi, in this manual you can find how to activate other PDO

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=0198441113779_LXM32A+CANopen_EN.pdf&p_Doc_Ref=0198441113779-EN

p.26 explane your problem:

With the default PDO settings, R_PDO1 and T_PDO1 are activated. The other
PDOs must be activated manually in order to be used.
A PDO is activated with bit 31 (valid bit) in subindex 01 hex of the respective
communication object. ......

Link to comment
Share on other sites

  • MVP 2022
2 hours ago, merttoprak said:

Could you please be more specific about where and how to configure the 31st bit of the relevant PDO ?

I do not know exactly how to do it in Lexium 32.  But i know that Schneider  PLC has some unique sequence for operate with VFD and Servo.

You can try to do something like decribed on p.50.

 

See chapter --- An initialization sequence must be written to start the operating mode---

I think for sw on something Schneider servo need to send commant for sw off this option before.

Then default ON value is ignored. OFF must be sended before send ON.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...