labytis Posted May 9, 2022 Report Posted May 9, 2022 Hello, im using PLC v350-35-T2 device. Trying to get response from device, but nothing works. i tried using wireshark to catch what bytes VisiLogic are sending and I got this: /00IDED eRaN$lIoR~bEnNy@KfIr eRaN$lIoR~bEnNy@KfIr Wanted to ask, why is it sending eRaN$lIoR~bEnNy@KfIr ? In protocol documentation it says, that all messages should start with /
MVP 2023 kratmel Posted May 9, 2022 MVP 2023 Report Posted May 9, 2022 Please try to use Info mode for test TX and RX messages in hex on HMI.
MVP 2023 kratmel Posted May 9, 2022 MVP 2023 Report Posted May 9, 2022 Toucn on HMI for 4-5s Info mode appear, default Password 1111.
labytis Posted May 9, 2022 Author Report Posted May 9, 2022 Thanks, really helped. It turned out baudrate is set to 57600, i tried with 115200 all the time