roghenr Posted July 8, 2022 Report Posted July 8, 2022 I succeeded in writing frequency data to the yaskawa drive for speed change. but I was not successful in reading the status bits from Run,Ready...and others. Could you give me a hint on how to read these bits? this drive does not mention read bits,coil but only registers. how to read individual bits and show on display. I'm using a mink 130. Thanks for any help, no idea how to do it For writing I used this FB
MVP 2023 kratmel Posted July 8, 2022 MVP 2023 Report Posted July 8, 2022 You must try to read two status byte from VFD. Best way - read it via PC for test. Then use the same modbus commmand in PLC. You can use "numeric to bit" function for convert VFD status bytes to 16 bit long vector in PLC.
roghenr Posted July 8, 2022 Author Report Posted July 8, 2022 3 horas atrás, kratmel disse: Você deve tentar ler dois bytes de status do VFD. Melhor maneira - leia-o via PC para teste. Em seguida, use o mesmo comando modbus no PLC. Você pode usar a função "numérico para bit" para converter os bytes de status do VFD em um vetor de 16 bits no PLC. obrigado pela ajuda vou tentar fazer Estou fazendo um teste e não entendo porque colocar os quatro mbs em 1 não deu um total de 15 #EDIT: nevermind, already found the issue