bbcxo Posted December 3, 2022 Report Share Posted December 3, 2022 Hello, I was seeing if someone could post logic/code on how to get the temperature reading from the sensor and then how to display the reading onto the HMI. Also, how to wire the sensor on the plc PT100: https://www.amazon.com/Pt100-Temperature-Sensor-Probe-Thread/dp/B074NVDCC4 PLC: v700 Snap on: V200-18-E3xb Thanks! Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted December 3, 2022 MVP 2022 Report Share Posted December 3, 2022 How to connect PT100 sensor on page 6 https://www.unitronicsplc.com/wp-content/uploads/2015/12/V200-18-E3XB.pdf how to set jampers for PT100 - please see page 9 of the same pdf. Please read this topic about PT100 1 Quote Link to comment Share on other sites More sharing options...
bbcxo Posted December 3, 2022 Author Report Share Posted December 3, 2022 @kratmel No logic is needed to display the temperature reading on the HMI? Quote Link to comment Share on other sites More sharing options...
MVP 2022 kratmel Posted December 3, 2022 MVP 2022 Report Share Posted December 3, 2022 8 minutes ago, bbcxo said: No logic is needed to display the temperature reading on the HMI? Yes. Only set Analog Input MI... in Hardware Config and place number on screen with the same MI. 1 Quote Link to comment Share on other sites More sharing options...