bbcxo Posted December 3, 2022 Report Posted December 3, 2022 Hello, I was seeing if someone could post logic/code on how to get the temperature reading from the sensor and then how to display the reading onto the HMI. Also, how to wire the sensor on the plc PT100: https://www.amazon.com/Pt100-Temperature-Sensor-Probe-Thread/dp/B074NVDCC4 PLC: v700 Snap on: V200-18-E3xb Thanks!
MVP 2023 kratmel Posted December 3, 2022 MVP 2023 Report Posted December 3, 2022 How to connect PT100 sensor on page 6 https://www.unitronicsplc.com/wp-content/uploads/2015/12/V200-18-E3XB.pdf how to set jampers for PT100 - please see page 9 of the same pdf. Please read this topic about PT100 1
bbcxo Posted December 3, 2022 Author Report Posted December 3, 2022 @kratmel No logic is needed to display the temperature reading on the HMI?
MVP 2023 kratmel Posted December 3, 2022 MVP 2023 Report Posted December 3, 2022 8 minutes ago, bbcxo said: No logic is needed to display the temperature reading on the HMI? Yes. Only set Analog Input MI... in Hardware Config and place number on screen with the same MI. 1