Salman Posted December 12, 2022 Report Share Posted December 12, 2022 Hi all, I have an old project file which was built with V430 and IO Expansion module IO-AI4-AO 2 and UN-IO-DI8-RO4. In this project file, the PLC takes in Analog Input as a current signal and outputs a voltage signal using the IO-A14-AO2 and the UN-IO-DI18-RO4 is used for monitoring of alarms and relays. Now, I want to shift to V560 and replace both IO Expansion modules with a SNAP IN module. Is it possible to change only the hardware in the HW Configuration panel, instead of doing it again for the new system? Thanks Quote Link to comment Share on other sites More sharing options...
MVP 2021 Flex727 Posted December 12, 2022 MVP 2021 Report Share Posted December 12, 2022 Generally yes. The restrictions are (off the top of my head) you can't convert directly between color and monochrome HMIs, Vision & Enhanced Vision products, or Samba and anything else. Since the V430 and V560 are both color HMI and Enhanced Vision, you should be good. However, you will have to convert all your I/O addressing, but that isn't difficult - just do "Replace Operand". You will have a problem with screen resolution, however. You will need to move or convert your graphics to fit on a 320x240 pixel screen. Your V430 has a 480x272 pixel screen. It will let you convert, but every screen element beyond 320x240 will be deleted when moving from V430 to V560. Just do all your HMI work before converting in the Hardware Config. Quote Link to comment Share on other sites More sharing options...
DanT Posted December 13, 2022 Report Share Posted December 13, 2022 Hi; In addition to the above, you will also have to set up the Analog Inputs and Outputs in the IO-Ai4-AO2 Modules. These are not automaticaly transfered when changing PLC types. Note the setup in the Old systems, redo in the new. DanT Quote Link to comment Share on other sites More sharing options...