Ichirou Posted September 7, 2016 Report Share Posted September 7, 2016 Hi there, i'm not able to read 32bit float big-endian from Janitza UMG104. Connection is over COM1 in Modbus mode, periodic trigger activated by pushbutton and set slave-name (bit) to 1. This works fine for the Modbus TCP slave, which provide me system information. The powermeter i try to read, deliver me important informations which i later need to add together with sensor values to a data table. Reading fails at the point, the 32bit float comes in. I tried: Register addresses 19018 (current, A), 19026 (power, W) and 19034 (power, VA) with own Tags as REAL, with memory float array MF[MF_0] to MF[MF_2], reading the registers from normal table (1639) and with adding address value for little endian communication. Nothing works. Registers 19xxx provide most used values. The REAL goes to a REAL to INT converter, ouput is INT32. A try with GridVis and Janitza Modbus Diagnostic tool works fine, all 3 Register addresses with reading 4 bytes. When i take a look the the online state of the memory floats, i see flickering data. I will try the swap bytes extended, but i hope, you have generally an idea, what goes wrong and how i can fix this. Pictures follows later, when i'm back to work Enviroment: Janitza UMG104 (latest firmware), Unistream USP-156-B10 (latest firmware), Com1 38400/8/n/1 Modbus periodic, Modbus Slave ID 1. (yes, I'm new to PLC/HMI) BR Quote Link to comment Share on other sites More sharing options...