  1. When I try to start visilogic, I get a message that says : VisiLogic was not shut down properly. Press OK to recover. When I press OK, I get a box with this info :

    Message Number: -2147220898

    DLL Name: UnPrHnd1

    Class Name: clsDbHandle

    Function Name: OpenConnection

    Label Name: errOpenConnection

    Details: Error opening connection

    Not a valid password

    Any help would be greatly appreciated.

    Thanks

  2. Sorry I have taken so long to get back to this. This project got put on the back burner for a while. I have a Red Lion G306 Touch panel that I am using to communicate with The V230 PLC's. The G306 is set up as the Unitronics master and is writing to and reading an integer file via RS-485. The two PLC's at the end of my network (farthest from the G306 master) communicate just fine. The two nearest the G306 do not communicate at all. There is about 30 ft between the G306 and the first two PLC's and about 20 ft between the first two and the last two. On the V230 closest to the G306, SI 88 (Connection status:COM 3) is flashing -32768 while the other three V230's show 0. The V230 next to that one shows SI 85 (Error Code COM 3) as 15 while the others show 0. Any Ideas?

    Thanks

×
×