Yes, mainly for monitoring engine and gearbox ECUs using V130 and V570.
J1939
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
Hi Mckruger,
You need to get a copy of the SAE J1939-71 standard to ascertain which PGN contains the parameter that you require.
For example Oil Pressure is byte 4 of PGN 65263, it is transmitted at 500ms intervals and has a default priority of 6.
The units are kPa with a resolution of 4 units/bit.
If you have the manuals for the truck you are working on the information should be in them.
Once you have entered the information in the configuration the rest is taken care of by Visilogic.
I hope this is of some use to you.