Posts posted by nagaraj

  1. Are all the thermocouples showing an error or only the ones immersed in water? Are you connecting the thermocouples directly to the PLC? If you are using more wires as extensions, you will be creating more junctions and you will definitely see an error. Also, make sure only the tip of the thermocouple is immersed in water and not the insulation. We use thermocouples in our units all the time and I have found it to be better to linearize the output from the thermocouple using reference temperature at least 30 deg C apart rather than using the thermocouple output directly.

  2. You are right. Thank you very much. Do you think the SB3 method will accumulate errors?

    Why wouldn't "elaspsed time" have anything to do with the RTC??

    When the start condition happens store the RTC in a variable.

    Now have a Subtraction function block that takes the current value of the RTC, subtracts the Start value, and places into another variable (your elapsed time).

    That is the most accurate elasped time you will be able to get.

×
×