  1. Tried the 120-22-R1,

     Configured the analog in on the module, setup the linearization, now it just reads zero.

    With volt meter tapped off the banner output I can read the mA out.

     

    cannot upload photo,

     

    Using diagram above - i have the banner ezarray powered from the terminal strip on the PLC. Brown 24+, blue 24-, gnd to gnd, White wire splits and goes to AN on 120, and red lead on Meter, Black lead tapped into 24-.

     

     

     

     

  2. I am having trouble seeing the bits on my input.

     I am using a Banner EZ Array 4-20Mah (White wire on Dia.)  into  I6, I setup up the linearization in the ladder to MI0. When online veiw the MI blinks intermittently 0 and 1.  I have another facility sending me one of their V120 to see if I may have a faulty unit. I have tested the EZ Array and know it is outputing the 4-20 signal. 

    Both the EZ Array and the plc are on the same 24VDC power source.

     

    post-44167-0-80495300-1445518756_thumb.jpg

    post-44167-0-51194500-1445518757_thumb.jpg

×
×