Hi,
I want to run CreateComm() in Excel 2016 with UnCmDrv1.dll.
I have check in References VBA Project, VB 6 Components.
Where is mistake?
Martin
-
Hello , my guestion is:
Can I use Unistream for controling two steppers motors like in Visio 430-J-TR34(PTO)?
We manufactured one machine with this Visio systém. I used predefined bloks and it was OK.
Is something like PTO in Unisteam? Is sample for direct controling two steppers morors?
Thanks Martin
- 1
-
I have problem with output. Life expectancy for UID - 0016R is 100k. How many times can I switch the relay output in this unit?
Thanks
Martin
UID0016R -
-
I need to drive axis motion with continuous change. I do not want to stopped after the end of the track, but continued without stopping.
It is possible through the PTO?What hardware can I use for it?
Can I use stepper or servo?Martin
-
I need to drive axis motion with continuous change. I do not want to stopped after the end of the track, but continued without stopping.
It is possible through the PTO?
Can I use stepper or servo?
Martin
VFD Incorrect CRC
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted · Edited by MartinIT
1. Communication cale has a shield. Conection according the manual.
2.Motor has a shield.
3.VFD has corecly gounded.
4. Comunication OK when VFD stoped. MI2322=0.
When hte motor is running - MI2322 has 4,5,10( MI2322 = 4,5,10, 4- Master-Time Out,5-No Comunication,10-Incorect CRC)
1.Can be wrong the VFD parameters setting? My parameters: VFD- P14.00-1,P14.01- 4, P14.02-1,P14.03-100,P14.04-0.0s,P14.05-0
2.Can be wrong the config parameters ? My config is: Com2,19200,0.5,8,E,1,RS485
Martin