  1. On 10/31/2016 at 8:45 AM, Joe Tauser said:

    Make sure your baud rate is set to 115200 if you are trying to talk to a V350.

     

    Joe T.

    I'll give that a shot.  I had it set to 19200, which is what the modbus communicates in, but I also noticed that when it switches to PCOM mode, it's displaying as 9600 baud on the SERIAL page of info mode.

    Mostly unrelated, but we also had one of them lose it's programming during a power outage yesterday.  I'm assuming I'd be able to copy the program from one to the other via microsd, even if it's password protected, correct?  Haven't read up on the process for doing that.

  2. Checking back in.  Finally got the opportunity to plug into the controller.  Not much luck though.  Any operations in visilogic to try to upload or even things like get hardware info, etc return an error.  Watching from info mode, COM1 does switch to PCOM, 9600,n,8,1 whenever the laptop is trying to talk to it, but apparently is not responding in kind.  The cable seems to be good, as I can see MODBUS traffic in realterm.  Is this bland error the expected behavior if the PLC is locked down?

    Again, thanks for any assistance.

×
×