Thank you Flex727, I have sent the message on the support email as well, I will report here the conclusion. Martin.
-
Dear Support team,
I have the Unistream US5-B10-B1 OPLC. The factory default touch screen calibration is bad, hence I used the Touch Screen Calibration command from the Uniapps menu. It usually worked well, however on this peace of hardware after touching all the 5 points, it writes "Calibration Failed" and recommends to do it again or restart...I have tried it sereral times with the same result. Any recommendations?
Thank you,
Best regards,
Martin Sirovy.
-
The problem is solved - I did not noticed, that the minimal frequency in HSO mode is 6 Hz. Thank to the support for a fast response.
-
Hello,
I have Unistream 7 and I have problem with configuration of high-speed output of module UIS-WCB2. The high speed output 0O should be able to be configured up to 250 kHz using PWM mode.
According to help, I have configured in properties windows HS Block 1 to PWM - see screenshot. Then I have configured the struct B1 according to the screenshot, but it still does not work. The classical "slow" output using function PWM worked, however I can not get to work the high-speed 100 Khz+ output mode.
Thank you very much for any tips.
Best regards,
Martin Sirovy.
Unistream Touch Screen Calibration Always Failing
in UniStream: Hardware
Posted
The conclusion from Unitronics support - probably HW issue. However I tried it for the last time today before sending back and the calibration past with no problem. The only difference I see I did not have so dry fingers today as last time.