26 minutes ago, Cam said:
Your both constantly calling the main display which is what is causing the screen to flicker.
See net 1 in the original program, every time the PLC scans the logic it is going to load the Main display. (In a Vision unit we are talking every 4-5 mS) You can remove this net.
Also while net 2 works you should have it broken into 4 separate nets. Nets 7,9,11,13,16,18 in the Main routine should also be separated in to multiple nets( you can get abnormal operation with the way you've done it) I didn't check the other subroutines but any where you've done something similar should be broken in to multiple nets.
And why are you calling the displays from the ladder using MB's linked to touch properties?? If you click on the Links & Jumps tab while editing an HMI you can put your display calls there and not have them in your ladder.
Thanks so much but Please i dont understand what to be done, can someone just kindly help me edit this program to see where i made the mistake.
-
8 hours ago, berkaykaya said:
I add first scan display codes at your program.
This codes make every first scan load -Main Display-
I think when you look codes you will understand "what i wanna do"
Have a nice day!
Thanks very much but i tried this but not still working. its still flicking.
-
The version I used is 9.8.79 BETA.
-
Thank you everyone for the support. kindly find attached the program
-
please i downloaded my program to my plc V1040 and its not displaying. It is just blinking. i tried updating the OS and still didnt show and also i entered the info mode but still not displaying. please what can i do to solve this problem?
what can i do to make my screen display my program?
-
Truly all said is write and its what is giving me challenges.
what is the way out?
how is it meant to be arranged?
what is the basics behind this?
for the MLs, what is advisable to be used?
-
-
Good day, please i have been having problem with a program am writing just because i believe it too long so i split it into subroutine but still not working. i checked and followed examples on the program but trying to use it on mine but still not working. Please i need someone to enlighten me on this subroutine, making call and returning to the initial program.
Thanks
-
HI all,
Am so grateful for the support from you all. Thanks
Please i will like someone to help review this program if its good and can function but if any observation seen or noted for correction, kindly let known.
Regards -
please can i design a scada system on my HMI V1020? if yes please i will like to have a sample if anyone has. thanks
-
can i run or test my program online without the plc device?
-
Thanks Joe T you are very right, I have the idea but I don't know where and how to start and I go through the examples on the software but not getting the starting point. Please what can be done to this to help my zeal and level?
-
-
Thanks, for the subroutine, I worked on it but yet to get the function
I get that now, each logic for each rung.
For the alarm, I will latch the output.
For the comparison, I want to use the output of the 3 sensor to open or close a valve and that was why I did it that way but the fact that it is wrong, kindly advice how to go about it.
Also, for the subroutine, is it that each detector will be design In a subroutine or what ?
Please if you have any written program that you know I can learn from, kindly help attach to aid my learning.
Regards
-
-
Thanks so much, it helps me go a long way.
But another issue is the Alarm section, if i want to add a program that will trigger alarm at 50 degree, please how will i go about that?
-
Thanks for the response, am using a RTD type and the plc am using is V200-18-E1B.
will this also go in with a pressure transmitter and for the output, will i set a coil or just pick ML as the output?
is this correct?
-
please, how can i write an Analog program for a temperature transmitter design to shut a device once it attain 85 degree celcius.
Remote Operator And Access
in Remote Operator
Posted
Good morning, please i have a challenge on the 2 issues listed below;
1. I configured my unistream plc to ethernet and i was able to control it from a system to VNC but this is only when am around the facility using same IP with PLC but trying to access it from another region through another internet provider, it does not connect. please what is the way out so that i will be able to monitor and control remotely
2. I tried configuring the android remote operator but its just giving configuration error. what is the way out ?
Please i need a way out to make my process completed.
Thanks.