11 hours ago, kratmel said:
So, as I understand it, Adam has to read data from the V570 RS485 (or RS232) and broadcast it to the Ethernet.
Yes thats was the problem.
But faced with the many problems, i connected them. now i need to know my AI register adresses. (MI200,MI201,MI202,MI203)
Would you help me about this problem?
Thank you sir.
-
hi everyone,
I have a problem about my v570 controller. i am trying to communicate advantech adam 4572 rs485 to ethernet converter but cant reach.
i can see tx and rx packages at configuration utility when i scan the slave id (advantechs program) but cant find the modbuss adress in the program.
then later i am going to take this variables to my indusoft scada.
Trying for 3 days
Best regards.
V570 RS485 connection problem
in Vision & Samba PLC + HMI Controllers & VisiLogic Software
Posted
I solved this problem.
When you finished the rs485 to ethernet connection, open indusoft and add motcp driver. then in main driver sheet Station adress must be like this :
ip:port number:modbuss adress (example 192.168.1.1:502:25) and MI0's register adress 4X:1 MI10's 4X:11 vs...
have a good day everyone