  1. G'day,

    I was wondering if it was possible to reset the keypad back to a display automatically.

    If someone say accidently presses  a variable numeric button and brings up the keypad  but doesnt hit enter I would like to have the keypad screen reset back to the last display automaitcally after a set time.

    Is this possible?

     

     

  2. You should have no problem running a 4-20 mA signal 300 meters- the voltage drop will be very small and you can ignore it. The problem may by in the other PLC you are connecting to. If the 4-20 input on that PLC is isolated, it will work. Unitronics connects the negative of the analog inputs to the power supply negative (non-isolated), so if your other PLC is non-isolated the signal will end there. You will probably need a loop isolator between the two.

    Joe T.

    You were saying that unitronics dont have an isolated analog input. The specs on the v200-18-e3xb snap in i/o say that it has 4 isolated analog inputs, is this ok?

  3. I need to run a signal from a pressure transducer ( 4-20mA ) over a 300m distance before it gets to the analog input on the OPLC. Is this distance too long?

    At the moment the transducer supplys an input for a different PLC which is located near the transducer. Can I parallel off this input and run the signal to my V570-57-T20B 300m away ?

    If its a matter of using the right size cable then what size would suite ?

×
×